Export cable (August 20th, 2019)

    WOZ_RVO.nl
    • Public
    Asked by WOZ_RVO.nl 83 days ago Answers (1)

    The export cable (TenneT) that crosses the HKNWFZ location (East to west) doesn’t seem to have a documented 500m boundary/corridor. Is it acceptable to have foundations and construction vessels closer than 500m to this cable (as long as the existing maintenance zone (stated in Appendix C) are not violated )?

    1 answer

      • WOZ_RVO.nl
        • Public

        WOZ_RVO.nl 83 days ago

        That is correct. TenneT decided to reduce the spacing between the cables to 200 metres. The spacing between the TenneT cable and the telecom cable remains 500 metres, hence the total zone between the two parcels is 500+200+500+500= 1,700 metres.
        Construction vessels are allowed within the whole Wind Farm Zone, with the restriction that jack up operations are prohibited in maintenance zones of existing cables and pipelines.